What size copper conductors are needed to supply a 3-phase, 208-volt, 200-ampere load at a distance of 250 feet with a maximum of 3% voltage drop?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the appropriate size of copper conductors needed to supply a 3-phase, 208-volt, 200-ampere load located 250 feet away, while maintaining a maximum voltage drop of 3%, several steps are considered based on electrical principles.

First, it is important to calculate the allowable voltage drop. For a 208-volt system, 3% translates to:

[

0.03 \times 208 \text{ volts} = 6.24 \text{ volts}

]

So, the conductors must be able to carry the load while ensuring the voltage drop does not exceed 6.24 volts.

Next, we use the formula for calculating voltage drop in a 3-phase system, which is given by:

[

V_d = \frac{ \sqrt{3} \times I \times L \times R }{1000}

]

Where:

  • ( V_d ) is the voltage drop,

  • ( I ) is the current (200 Amps),

  • ( L ) is the one-way length of the conductor (250 feet, but for a round trip, you double it for the formula, giving you 500 feet), and

  • (