What minimum size ungrounded THHN conductors are required for a 120/208-volt, 3-phase feeder supplying continuous load of 37.5 kVA?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the minimum size ungrounded THHN conductors required for a 120/208-volt, 3-phase feeder supplying a continuous load of 37.5 kVA, it’s important to first calculate the current that the feeder will carry under these conditions.

The formula for calculating current in a three-phase system is:

[

I = \frac{P}{\sqrt{3} \times V}

]

where:

  • (I) is the current in amperes (A),

  • (P) is the power in watts (W),

  • (V) is the line voltage (in this case, 208 volts).

Given that the load is 37.5 kVA, we convert this to watts for use in our formula:

[

P = 37.5 , \text{kVA} \times 1000 = 37500 , \text{W}

]

Now, inserting the values into the formula:

[

I = \frac{37500 , W}{\sqrt{3} \times 208 , V}

]

Calculating this step-by-step:

  1. Calculate (\sqrt{3}): Approximately 1