What is the minimum standard size overcurrent protective device required for a 120/208-volt, 3-phase feeder supplying a continuous load of 37.5 kVA?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

In electrical installations, it's crucial to determine the appropriate size of overcurrent protective devices to ensure safety and compliance with national electrical codes. For a continuous load, you need to apply certain rules regarding sizing.

First, calculate the load in amperes using the formula:

[

\text{Amperes} = \frac{\text{kVA} \times 1000}{\sqrt{3} \times \text{Volts}}

]

For a 120/208-volt, 3-phase feeder with a continuous load of 37.5 kVA, this is calculated as follows:

[

\text{Amperes} = \frac{37.5 , \text{kVA} \times 1000}{\sqrt{3} \times 208 , \text{V}} \approx 104.1 , A

]

Since this load is continuous, the National Electrical Code (NEC) requires that overcurrent devices must be sized to handle continuous loads at 125% of their maximum rating. Therefore, the appropriate size calculation is:

[

\text{Minimum Overcurrent Device Size} = 104.1 , A \times 1.25 \approx 130