What is the minimum standard size inverse-time circuit breaker for a 480-volt, 3-phase circuit with a 50-kilowatt continuous load?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the minimum standard size inverse-time circuit breaker for a 480-volt, 3-phase circuit with a 50-kilowatt continuous load, you begin with calculating the full-load current (IL) using the following formula for 3-phase circuits:

[

IL = \frac{P}{\sqrt{3} \times V \times PF}

]

Where:

  • ( P ) is the power in watts (50 kW = 50,000 watts)

  • ( V ) is the voltage (480 volts)

  • ( PF ) is the power factor (assumed to be 1 for continuous loads unless specified otherwise)

Substituting the given values into the formula:

[

IL = \frac{50000}{\sqrt{3} \times 480 \times 1}

]

[

IL \approx \frac{50000}{831.76} \approx 60.0 \text{ Amps}

]

Now, voltage drops for continuous loads typically require applying a 125% rule for the breaker size to ensure that the circuit can handle overload conditions without nuisance tripping. The calculation for the circuit breaker size thus becomes:

[

Breaker Size = IL