What is the minimum size EMT needed for a combination of six 1 AWG, eight 2 AWG, and four 1/0 AWG THW conductors?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the minimum size EMT (Electrical Metallic Tubing) required for a combination of conductors, we need to calculate the total cross-sectional area of the conductors and then refer to the NEC (National Electrical Code) guidelines for conduit fill.

  1. Calculate the cross-sectional area of each type of conductor:
  • 1 AWG THW conductor has a cross-sectional area of approximately 0.1257 square inches.

  • 2 AWG THW conductor has a cross-sectional area of approximately 0.0785 square inches.

  • 1/0 AWG THW conductor has a cross-sectional area of approximately 0.1671 square inches.

  1. Multiply the number of each conductor by its respective cross-sectional area:
  • For six 1 AWG conductors: ( 6 \times 0.1257 ) = 0.7542 square inches.

  • For eight 2 AWG conductors: ( 8 \times 0.0785 ) = 0.628 square inches.

  • For four 1/0 AWG conductors: ( 4 \times 0.1671 ) = 0.6684 square

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy