What is the minimum size allowable for a conductor in a circuit with a continuous load at 30 amperes?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

In determining the minimum size allowable for a conductor carrying a continuous load, it’s important to refer to the National Electrical Code (NEC), which establishes guidelines for electrical installations. A continuous load is defined as a load that has a duration of three hours or more.

For a continuous load at 30 amperes, you must consider a derating factor to ensure safe and efficient operation. The NEC requires that conductors carrying continuous loads be sized at 125% of the load current. Therefore, for a 30-ampere load, the calculation is as follows:

30 amperes x 1.25 = 37.5 amperes.

Now, we must refer to the NEC Table for allowable ampacities of various conductor sizes. According to the NEC, a 4 AWG copper conductor typically has an allowable ampacity of 85 amperes, which is more than sufficient for a load of 37.5 amperes. In contrast, larger gauge conductors, such as 6 AWG and 8 AWG, have lower ampacity ratings (likely around 65 and 50 amperes respectively), and would not meet the requirements for this continuous load application.

Thus, since 4 AWG is the minimum size that