What is the minimum size THWN-2 ungrounded feeder conductor required to supply a dwelling unit with a load at 110°F?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the minimum size THWN-2 ungrounded feeder conductor required for a dwelling unit with a specific load at 110°F, understanding the relevant ampacity tables from the National Electrical Code (NEC) is crucial. The ampacity of conductors is influenced by the ambient temperature to which they are exposed. For THWN-2 conductors, the ampacity is reduced as the temperature increases.

At 110°F, the calculated ampacity of a conductor is lower compared to standard conditions (usually 30°C or 86°F). Specifically, the ampacity for THWN-2 conductors needs to be adjusted according to temperature correction factors provided in the NEC.

Based on load requirements and considering the temperature factor for THWN-2 conductors at 110°F, a 1 AWG THWN-2 conductor typically has an ampacity that meets the needs of a standard residential load. Conductors of smaller gauge sizes (like 2 AWG or lower) would not adequately support the necessary load, while larger sizes (like 2/0 AWG) would be more than sufficient but exceed the minimum requirement.

Using ampacity charts, one can confirm that a 1 AWG THWN-2 ungrounded