What is the maximum length for a single-phase, 110-volt branch circuit with a 40-ampere load using 6 AWG aluminum conductors?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the maximum length for a single-phase, 110-volt branch circuit with a 40-ampere load using 6 AWG aluminum conductors, it is essential to consider voltage drop and the permissible limits set by the National Electrical Code (NEC).

In general, a voltage drop of 3% or less is ideal for branch circuits, which would allow for efficient operation of electrical devices. For a 110-volt system, this means the allowable voltage drop should not exceed 3.3 volts (which is 3% of 110 volts).

To find the maximum length of the conductor, we can use the voltage drop formula:

[ \text{Voltage Drop} = \frac{2 \times L \times I \times R}{1000} ]

Where:

  • L = one-way length of the circuit in feet,

  • I = load current in amperes,

  • R = resistance of the conductor per 1,000 feet.

For 6 AWG aluminum wire, the resistance is approximately 0.395 ohms/1,000 feet. By rearranging this formula to solve for L (the one-way length), we can find the maximum allowable length before the voltage drop becomes excessive.