What is the ampacity of a 10 AWG THWN copper conductor when terminated to a circuit breaker with a maximum temperature of 60°C?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the ampacity of a 10 AWG THWN copper conductor when terminated to a circuit breaker rated for a maximum temperature of 60°C, reference to the National Electrical Code (NEC) is necessary. Ampacity refers to the maximum amount of electric current a conductor or device can carry before sustaining immediate or progressive deterioration.

According to NEC Table 310.16, the ampacity of copper conductors is rated based on their temperature ratings. For a 10 AWG copper wire, the base ampacity at an ambient temperature of 30°C is typically listed as 30 amps when using THWN insulation.

However, for conductors operating at a higher maximum temperature rating, such as 60°C, the ampacity needs to be adjusted based on the circuit breaker and insulation ratings. In this case, even though the base ampacity is 30 A, since the breaker has a maximum termination temperature of 60°C, adjustments may lead to different considerations, but in this scenario, the ampacity remains at the nominal 30 A because THWN insulation effectively supports this rating without derating under typical conditions when referenced to the circuit breaker's limitations.

Therefore, the correct answer of 30 A reflects the established ampacity for a