What is the ampacity of a 12 AWG THWN-2 copper conductor when connected to a circuit breaker with a termination temperature of 60°C/75°C?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the ampacity of a 12 AWG THWN-2 copper conductor, one must refer to the National Electrical Code (NEC) tables, which provide ampacity ratings based on various factors, including conductor size, insulation type, and installation conditions.

For a standard 12 AWG THWN-2 copper conductor, under typical conditions, the ampacity is 20 A. However, it's important to consider the specific termination temperature. When connected to a circuit breaker with a termination temperature rating of 60°C/75°C, the ampacity can be adjusted according to the NEC guidelines based on the ambient temperature and the insulation type.

The adjustment factors for THWN-2 insulation allow for slightly higher ratings at the 75°C termination than at 60°C. As such, the ampacity for a 12 AWG THWN-2 conductor permits continuous loads at a rating of 25 A when accounting for these conditions. This makes the option indicating 25 A the correct choice, as it reflects the conductor's ability to handle that level of current safely under the specified termination temperature.

In summary, the ampacity of a 12 AWG THWN-2 copper conductor is influenced by both the conductor's size and type