For a 208Y/120-volt, 110-ampere feeder supplying a single dwelling unit, what is the minimum size THWN-2 grounded feeder conductor required?

Prepare for the Fundamental Code Calculations Test with engaging quizzes and exercises. Explore various question formats and receive instant feedback. Achieve excellence in code calculations with our comprehensive study materials and expert-designed exercises!

To determine the minimum size THWN-2 grounded feeder conductor for a 208Y/120-volt, 110-ampere feeder supplying a single dwelling unit, we refer to the National Electrical Code (NEC) tables for the allowable ampacity of conductors based on the material and insulation type. THWN-2 is a type of thermoplastic wire rated for high-temperature and wet locations.

According to NEC Table 310.16, conductors’ ampacity must be checked against the load they are expected to carry. For copper conductors with THWN-2 insulation, the ampacity can vary based on whether the conductors are in a raceway, free air, or bundled together.

For a residential feeder supporting a continuous load, it is common practice to apply a demand factor. However, since the load here is given as 110 amperes, we must ensure the conductor size accommodates the full load, taking into account any relevant derating factors.

For a 110-ampere load in typical conditions, a 3 AWG THWN-2 copper conductor is adequate as it can handle up to 100 amperes under typical conditions. However, because of the need to account for continuous loads where conductors may